Zones not running

Richard Snyder
Actualizado 2026-05-14 13:48:46 UTC
Tema: Solución de problemas
All zones are programmed to run but only zone 1 runs.
Ver: 534    Seguir: 0   

2 Respuestas    Haga clic en la respuesta para ver la respuesta completa y los comentarios.


Candice Wang
Actualizado 2026-05-27 02:42:07 UTC

Dear customer,

If all zones are programmed and shown as "running" in the app, but water only physically comes out of Zone 1, this is usually caused by a hardware or wiring issue rather than a software glitch.

Please try the following steps to isolate the problem:

  1. Check the Common Wire (C-Wire)

  2. Test Master Valve (MV) / Pump Settings

  3. Perform a Manual Test at the Valve Box

    • If water flows: The plumbing is fine, and the issue is strictly electrical (wiring or the Netro port).

    • If water does NOT flow: The main manual shut-off valve to those specific zones might be closed.

If the wiring looks perfect and manual testing works, please email us at support@netrohome.com with your serial number. Our team can check the electrical current logs to see if the controller is properly sending 24VAC voltage to the other ports.


Thanks,

Candice