If you do not have master valve, you may try put two zone wires in one slots. Please note that each valve open needs to consume about 300 am, and the Netro power adapter is 800 Am. If you have master valve, run two zones together (add the master valve) will over the limit.


Thanks,

Netro Inc

浏览: 3069    点赞: 0


Ritesh Nanda
2020-06-15 16:47:17  
Thanks , sorry not much familiar with irrigation system , when you say master value , you mean one extra valve on top of individual zones valve?
Netro Inc
2020-06-16 01:17:37  
Hi Ritesh,

Yes it is a extra valve on top of individual zones valve.