Netro Inc
更新时间 2019-08-01 00:58:11 UTC

Hi Hussein,


Can you use a "working" zone to control the low pressure station. If the problem remains I would suggest checking the valve.


Another way to troubleshoot: To test if the controller is working properly, use a multimeter (AC voltage mode) to test the voltage between the common wire and the zone wire when the zone is active. Normally the voltage should be between 24V and 28V.


Thanks,

Netro Inc

浏览: 1750    点赞: 0